VTS First Script

发布于:2024-05-18 ⋅ 阅读:(150) ⋅ 点赞:(0)

First Script

SECTION ReadProperty

TEST #1 ReadProperty AI1 present value

SEND (
   DA  = 192.168.10.74:47808
   PDU = Confirmed-Request
   Service = ReadProperty
   Object = 0, AI, 1
   Property = 1, present-value
)

EXPECT (
   SA  = 192.168.10.74:47808
   PDU = ComplexAck
   Service = ReadProperty
   Object = 0, AI, 1
   Property = 1, present-value
   OpenTag 3
      Real = -273.14999
   CloseTag 3
)

在这里插入图片描述

Improved

;-------------------------------------------------------------------------------
;  Read BACnet property datatypes to verify the decoder
;--------------------------------------------------------------------------------

;--------------------------------------------------------------------------------
SETUP

INCLUDE "config.vts"
; Specify the name of the device to be tested (as defined by VTS Names dialog)
IUT_ADDR = "IUT"

;--------------------------------------------------------------------------------
SECTION ReadProperty
TEST #1 ReadProperty AI1 present value

SEND (
   DA  = IUT_ADDR
   PDU = Confirmed-Request
   Service = ReadProperty
   Object = 0, AI, 1
   Property = 1, Present-Value
)

EXPECT (
   SA  = IUT_ADDR
   PDU = ComplexAck
   Service = ReadProperty
   Object = 0, AI, 1
   Property = 1, Present-Value
   OpenTag 3
      Real <= -273
   CloseTag 3
)

在这里插入图片描述